A size 14 AWG branch-circuit conductor protected by a 15-ampere circuit breaker supplying three 20-ampere duplex receptacles is:

Explanation:
In this scenario, a size 14 AWG branch-circuit conductor is being used with a 15-ampere circuit breaker to supply three 20-ampere duplex receptacles. The National Electrical Code (NEC) outlines specific requirements regarding the sizing and protection of conductors in relation to the devices they supply. A size 14 AWG conductor typically has a maximum ampacity of 15 amperes. The circuit breaker, designed to protect the wiring from overloads, is also rated at 15 amperes, providing appropriate protection for the conductor. However, the key issue arises with the receptacles being rated for 20 amperes. The NEC states that branch circuits supplying receptacles must have conductors that are adequate for the load. If the receptacles are rated for 20 amps, they can facilitate heavier loads, which presents a risk when paired with conductors rated only for a maximum of 15 amps. Since the circuit breaker will only trip if the current exceeds 15 amps, and the receptacles can potentially draw more power (up to 20 amps), there lies a fundamental issue of compliance. The receptacles could be used in a configuration where they draw more than what the conductor can handle safely. Because of

When preparing for the Journeyman Electrician Exam, one of the key areas you’ll need to wrap your head around is compliance with the National Electrical Code (NEC). So, let’s tackle a common question that may arise in your studies: A size 14 AWG branch-circuit conductor protected by a 15-ampere circuit breaker supplying three 20-ampere duplex receptacles is: A. Compliant with NEC B. Not in compliance with NEC C. Only compliant if devices are rated 15 amps D. Considered safe due to overload protection.

The answer? It’s B: Not in compliance with NEC. Now, why’s that significant? Well, understanding the relationship between conductor sizing and circuit protection is crucial for both your exam and your future career as an electrician. Let’s dig into why this situation raises a red flag.

A 14 AWG wire has a maximum ampacity of 15 amps. You’ve probably heard the term “ampacity” tossed around before, right? It simply refers to the maximum amount of electric current a conductor or device can handle before damage occurs. If you’re not careful, you might just overload that wire and create serious safety hazards—definitely not what you’ll want when working with electrical systems.

Now, couple that with a 15-amp circuit breaker, which, while it does offer some protection, only trips when the current exceeds its rating. Remember, a circuit breaker is like a safety net designed to prevent overloads—but if you’re connecting it to three 20-ampere receptacles, you’re asking for trouble. These receptacles can deliver more power than your wiring system can handle. Do you see the mismatch here?

Why does this matter? Well, let’s break it down. If someone connects a heavy load to one of those 20-amp receptacles, the demand could surpass the safe capacity of the 14 AWG wire. Since the circuit breaker won't trip until the current exceeds 15 amps, there’s a chance that the wire could overheat, posing significant risks like electrical fires. To your future clients and yourself—safety is everything!

By the NEC’s guidelines, branch circuits supplying receptacles must have conductors sufficient for the loads they might carry. When you set up a circuit, you must ensure that the wiring is compatible with the devices it’s meant to serve. In essence, the NEC is there to help you prevent catastrophic failures. It sounds kind of like a lifeguard at a pool, right? They ensure everyone’s safe—so you can swim without worry!

You might wonder, “What if I just use 15-amp receptacles instead?” While that could technically align with NEC regulations, it’s a bit of a band-aid approach. Compliance is not just about ticking boxes; it’s about ensuring everything fits together harmoniously and within safety parameters. Always remember: the goal is not just passing the exam but also ensuring safety and efficacy in real-world applications.

So, when preparing for your Journeyman Electrician Exam, keep your eyes peeled for these compliance queries. They might come dressed up in slightly different formats, but they all revolve around the same core principles. Think of it like assembling a puzzle—each piece is unique, but they all need to connect to create a complete picture. And in this picture, safety should always be at the forefront.

When you're studying, use examples like this to help solidify your understanding of codes and standards. Grab some study materials, hit up mock tests, and connect with fellow students or professionals in the field. You’re in this journey together, and having those discussions can really enhance your grasp of these critical concepts.

At the end of the day, whether you’re working with electricians or studying for the exam, remember that knowledge is power. The better you understand the regulations and requirements, the more equipped you’ll be to tackle any situation that comes your way. So, what are you waiting for? Get started on your studies, lift those wires—and let’s get you ready to shine on that Journeyman Electrician Exam!